Setting up a room that uses 15 amps of power without tripping circuit breakers or catching anything on fire

GEC: Discuss gaming, computers and electronics and venture into the bizarre world of STGODs.

Moderator: Thanas

Post Reply
User avatar
Dominus Atheos
Sith Marauder
Posts: 3904
Joined: 2005-09-15 09:41pm
Location: Portland, Oregon

Setting up a room that uses 15 amps of power without tripping circuit breakers or catching anything on fire

Post by Dominus Atheos »

The more I think about it, the more impossible it seems. There is a room that I would like to install several electronic devices in, but the circuit breaker is only rated for 15 amps. I'm pretty sure all of my stuff tuned on at once will draw more then 15 amps and trip the beaker. Worse than that, I also need to figure out what kind of power strips to get. There are only 2 outlets in this room, so I'm going to need a visio diagram to even plan this, and then figure out what extensions cables and surge protectors can handle the loads without catching on fire.

Help?
User avatar
LaCroix
Sith Acolyte
Posts: 5196
Joined: 2004-12-21 12:14pm
Location: Sopron District, Hungary, Europe, Terra

Re: Setting up a room that uses 15 amps of power without tripping circuit breakers or catching anything on fire

Post by LaCroix »

Most important - get someone who knows what you are dealing with - I have done a lot of wiring but I am not a licensed professional, and I am not aquainted with US electrical infrastructure, apart from the basics.

I'm not sure what electric standards you are using, but one outlet (European standard) is usually rated at ~3500 watts over here - 240V and 15 amps max. (Do not assume his would mean that a similar standard outlet should be fine to run 30 amps at 110V. It most likely isn't.) Also, having a circuit breaker installed with 15 amps rating means that whoever installed that does believe you shouldn't use that much, which implies each outlet should at maximum only be able to handle sligtly less than 15 amps. (~1600-1800 watts @ 110-120 V)

It seems a bit low wattage to me - though, my vacuum cleaner takes 2000Watts, but then again, if run on 110V, it would only consume a 1000 watts.

Anyway - running that much current (the max xour cb allows) long term through a single outlet is not sensible though. Cables do get hot when current is drawn.

I am assuming the worst case - your outlets are both wired to the same fuse in the box, so my suggestion would be to run a second set of wires through the hoses, and wire one of the outlets to it's own fuse. This has to come first, or you are risking cable meltdown inside the wall.

Apart from preventing y house fire, that measure distributes power between outlets and causes colder wires, which cause less resistance and less amps flowing in total.

This might already be enough to let the cb be fine with it, as long as you do switch on the devices one by one or group by group, slowly, to avoid the peaks in power most appliances do have on startup.

Second step if that is not enough - get a stronger cb installed, after checking with an electrician if your line to the house will be fine with it (we do have standards over here that require 50-100 amps nominal for the main, but I don't know how that is in the states/your hometown. )

Do not go overboard - stick to the minimum needed, because you are risking the cb not breaking a single outlet being overloaded (which it is among other things designed for). I would recommend 20 amps.
A minute's thought suggests that the very idea of this is stupid. A more detailed examination raises the possibility that it might be an answer to the question "how could the Germans win the war after the US gets involved?" - Captain Seafort, in a thread proposing a 1942 'D-Day' in Quiberon Bay

I do archery skeet. With a Trebuchet.
User avatar
Alferd Packer
Sith Marauder
Posts: 3706
Joined: 2002-07-19 09:22pm
Location: Slumgullion Pass
Contact:

Re: Setting up a room that uses 15 amps of power without tripping circuit breakers or catching anything on fire

Post by Alferd Packer »

I'd get a surge protector with a long cable, rather than an extension cord and a surge with a short one. I use this Belkin model a lot at work, because it's robust and it guards against the shitty wiring in our building. It's actually a violation of the fire code in our jurisdiction to use extension cords, so this model's long cable really helps.

Also also, if you're in a residential building, especially an older one, odds are good that outlet shares a circuit with some others. You should test other nearby rooms/light fixtures, if you haven't already.
"There is a principle which is a bar against all information, which is proof against all arguments and which cannot fail to keep a man in everlasting ignorance--that principle is contempt prior to investigation." -Herbert Spencer

"Against stupidity the gods themselves contend in vain." - Schiller, Die Jungfrau von Orleans, III vi.
User avatar
Napoleon the Clown
Jedi Council Member
Posts: 2446
Joined: 2007-05-05 02:54pm
Location: Minneso'a

Re: Setting up a room that uses 15 amps of power without tripping circuit breakers or catching anything on fire

Post by Napoleon the Clown »

Not the answer I suspect you want, but I am going to suggest you contact an electrician to have more outlets professionally put into the room. Tell the electrician your plans so that they can get things set up in a manner that won't start fires. It'll be expensive, but much less expensive than burning down your house. And it'll be done in a way that no circuits are drawing 15 amps.
Sig images are for people who aren't fucking lazy.
User avatar
Sea Skimmer
Yankee Capitalist Air Pirate
Posts: 37390
Joined: 2002-07-03 11:49pm
Location: Passchendaele City, HAB

Re: Setting up a room that uses 15 amps of power without tripping circuit breakers or catching anything on fire

Post by Sea Skimmer »

What are you actually trying to plug in? A 15 amp sustained draw at 115v is considerable.
"This cult of special forces is as sensible as to form a Royal Corps of Tree Climbers and say that no soldier who does not wear its green hat with a bunch of oak leaves stuck in it should be expected to climb a tree"
— Field Marshal William Slim 1956
Post Reply